    GFCI - mini splits

    We finally got our mini split AC installed. It's a 120 volt system and is designed to be on a 15 amp breaker. Our dock has a 30 amp GFCI breaker and when ever the outside unit comes on it trips that breaker. Inside the boat it's connected to a 15 regular breaker and it doesn't kick. The fan on the outside unit will only turn about 5 revolutions so I'm sure it's a GFCI issue not an over load.
    We have #10 wire running to the outside unit and after problems we hooked up a second ground. Nothing fixed the problem. I'll be headed back down later today with a generator to see how it runs when I hook it up to that.
    The inside unit gets it's power from the outside unit and we can run the fan as long as we want.
    I've been told because it's an inverter unit this creates issues with GFCI breakers.
    Any thoughts??

  2. #2
    Junior Member
    Join Date
    Feb 2016
    Posts
    9
    Everything runs with the generator, the unit only pulls 6 amps.
    Amy thoughts?

  3. #3
    Senior Member easttnboater's Avatar
    Join Date
    Nov 2002
    Location
    GA
    Posts
    654
    There have been many reports out on the Internet of marinas installing GFCI breakers that trip constantly. You are going to have to talk with the marina.

  4. #4
    Senior Member Endurance's Avatar
    Join Date
    Nov 2005
    Location
    Lake Powell, Utah
    Posts
    270
    I don't know it it's available at your marina, but it would be an interesting troubleshooting exercise to plug into other 30A GFCI breakers. Perhaps using a neighbor's power or another dock you could find one.

  5. #5
    Junior Member
    Join Date
    Feb 2016
    Posts
    9
    I should be able to get to another GFCI this week end. I'll post the results.
    Thanks

  6. #6
    Junior Member
    Join Date
    Feb 2016
    Posts
    9
    Due to the rains and mother in law in the hospital we didn't get to go this past weekend.Maybe this coming weekend will play out better.

  7. #7
    Member
    Join Date
    Jul 2012
    Location
    Pacific Northwest
    Posts
    97
    GFCIs are designed to trip if there is an imbalance between the input and the output. In english that means, if the current in the black hot wire is not the same as the current in the white neutral wire then the GFCI trips. The reasoning behind this is that if an imbalance occurs then current is leaking somewhere in the system. If the GFCI on the dock trips the imbalance can be on the dock, or on the boat. It also means that the current is leaking into the water surrounding the boat or the dock and this is an extremely dangerous situation. So, the leakage needs to be isolated. How is that done. Unplug from the shore tie. Turn off everything on the boat. Plug in. If the GFCI trips the problem is on the dock. If not, then, one at a time, turn on the circuits on the boat. When the GFCI trips you have found the circuit that has the problem. Unplug. Turn everything off again. Turn off each individual appliance on the faulty circuit. Plug in. turn the circuit breaker for the faulty circuit on. If the GFCI trips it is the wireing. If not turn on each item one at a time. When the GFCI trips you have found the culprit.

    Also. A lot of marinas are installing these on old systems that have not been adequately tested for leakage. If the problem is on the dock the marina needs to get an electrician in to troubleshoot the entire dock electrical system. That is a big job and not cheap to do. But needs to be done. Boat owners at the marina should insist on it, or go somewhere else.

    Inverters can be an issue. Some inverters have been found to be wired incorrectly in regards to ground. The grounds for the AC side of the inverter and the DC side should not be connected inside the inverter. Unfortunately some have been found to be connected. This will trip your GFCI. Why. If the grounds are connected you have just connected the water around your boat to AC. Mkae sure your inverter is wired correctly. see http://www.xantrex.com/documents/Tec...-Universal.pdf (see the last question) see also http://www.qualitymarineservices.net...%2012-2005.pdf
    Last edited by Ike; 09-08-2017 at 05:25 PM. Reason: addedcinfo.

  8. #8
    Junior Member
    Join Date
    Feb 2016
    Posts
    9
    Thanks for the reply's, I used this information to determine that my inverter on the boat is wired correctly. What I'm being told is because my AC mini split also uses an inverter, the way the inverter starts the motor in the outside unit using capacitors which store and then discharge electricity this causes the gfci to trip. My plans at the moment are to install an marine isolation transformer on the boat. These are made to prevent galvanic corrosion by separating the boat power from the shore power. I talked to one of the manufacturers and they said with the issues I'm having the isolation transformer should take care of the problem. A little pricey but it beats trying to sleep when it's 85 degrees!!! I'll post once I get everything installed, which will take a little while and let everyone know how this works out.

  9. #9
    Member
    Join Date
    Jul 2012
    Location
    Pacific Northwest
    Posts
    97
    An isolation transformer is the way to go. It literally isolates the power on your boat from the power ashore. I hope it solves your problem.

  10. #10
    Senior Member easttnboater's Avatar
    Join Date
    Nov 2002
    Location
    GA
    Posts
    654
    Isolation transformers are more than a "little" pricey. It should solve your issue. However, as far as I know, all HVAC systems use a capacitor or series of capacitors to help start the compressor. Every HVAC unit that I have had on my houseboats have used capacitors and have not tripped a GFCI.